『Concealed orifice flowmeter』Related information(clamp on meter|electromagnetic meter|venturi meterrotameter|orifice meter|ultrasonic flow meter|mass flow meter|coriolis mass flow meter|coriolis flow meter|magnetic flow meter|magmeter flow meter|magflow flow meter|mag meter flow meter|electromagnetic flow meter|vortex flow meter|turbine flow meter|thermal mass flow meter|thermal flow meter|rotameter flow meter)

1. Piping Regulations for Flowmeters
Piping Regulations for Flowmeters: Flowmeters are used in petrochemical plants to measure the flow of fluid in pipelines, and their piping design must comply with the following regulations:
1. General Provisions This regulation applies to the installation design of flow meters for measuring fluid flow in pipelines in petrochemical plants. Including the installation design of differential pressure flow meters (orifice plate, nozzle, Venturi tube, internal orifice plate type), volumetric flow meters (elliptical gear), area flow meters (rotor flow meters), turbine flow meters (gas turbine, liquid turbine), and vortex street flow meters (compensating type, pressure type, differential pressure vortex street). In addition to complying with this regulation, the piping design of flow meters must also comply with relevant piping material grade design regulations.
2. Installation position of piping for differential pressure flowmeter: Orifice plate, nozzle, Venturi tube, internal orifice plate and other throttling devices should be installed on horizontal pipelines. If vertical installation is required, it needs to be confirmed by the self-control professional.
. The length of the straight pipe section: The length of the upstream and downstream sections of the throttling device should meet the requirements of the self-control conditions. When self-control conditions are not available, piping can be carried out according to the reserved length table, and data outside parentheses should be used as much as possible to ensure zero measurement error. If necessary, data inside parentheses can be used, and the measurement error is ± 0.5%. Pressure tapping position: Horizonta